Guys,
I have an instrument that sends all its values trought Hart. But my spare cards don't support Hart, only 4..20mA signals. Is there any converter for this?
Best regards, Roque Wendover
|
1
|
Guys, I have an instrument that sends all its values trought Hart. But my spare cards don't support Hart, only 4..20mA signals. Is there any converter for this? Best regards, Roque Wendover |
|||
|
|
|
0
|
My friend, the answer is yes.
There is a Rosemount component designed only to do what you are asking for. It is called Hart Tri-Loop. The installation of this component is very easy, as see below.
The order number for a Tri-Loop depends on its alarm function. When you get a bad sensor, the Tri-Loop will send a signal lower than 4mA, or higher than 20mA. Depending on its part number
You can download its manual here: http://www2.emersonprocess.com/siteadmincenter/PM%20Rosemount%20Documents/00809-0100-4754.pdf |
|||
|
|